Dear dchartier, actually this Profibus Devices are connected to Remote Panel , In remote Panel there is ET200M Module I have used. so could I directly Profibus Connection to next Profibus devices without using any Module.
|
Rajkiran Patil |
|
1/5/2012 2:49 PM | |
Joined: 9/27/2006 Last visit: 3/14/2025 Posts: 12344 Rating:
|
Hello rajkiran; Profibus-DP allows daisy-chained connection of u^p to 125 nodes on a network, so yes, you can easily extend the Profibus cable from one ET 200M (IM 153-2 imnterface module) to any other Profibus-DP slave (another IM 153-2, a Profibus-enabled drive, a Profibus encoder, a Profibus regulator...). Profibus connector have 2 entries for the Profibus cable, one entering the node, one exiting to the next node, so daisy-chaining is easy to implement. Actually the terminating resistance on the Profibus connector blocks transmission between the entering cable and the exiting calbe, thus isolating the node and cutting transmissions at that point. The main points are: maintaining the Profibus parameters of the bus (max. number of nodes per segment [32], max. busspeed per segment, use of repeaters to extend number of nodes and bus speed) and configuring all nodes to the master, in the Profibus configuration software. Have a look at the attached illustration of a typical Profibus configuration, it is extracted from the following manual: SIMATIC NET PROFIBUS Network Manual System Manual Hope this helps, Daniel Chartier |