2/21/2018 1:57 PM | |
Joined: 10/28/2014 Last visit: 3/11/2025 Posts: 63 Rating:
|
Hi electronics26, Refer below manual and check if all steps have been followed. Mainly the connection in NetPro and the server client bit in DB. https://support.industry.siemens.com/cs/ww/en/view/103447617 Also you could try downloading only the sample program and enure everything else is working fine. https://support.industry.siemens.com/cs/ww/en/view/109749851 Hope this helps! |
Last edited by: Jen_Moderator at: 2/21/2018 2:19:59 PMOptimized links |
|
This contribution was helpful to
1 thankful Users |
2/21/2018 3:00 PM | |
Joined: 3/9/2017 Last visit: 4/27/2023 Posts: 7 Rating:
|
Maybe someone can share example that includes CPU with using CP card as server for modbus TCP/IP. |
2/21/2018 5:50 PM | |
Joined: 10/28/2014 Last visit: 3/11/2025 Posts: 63 Rating:
|
Hi electrinics26 The link i posted earlier has a sample program. U only have to adjust your hardware config. Also as pointed out by Kaulquappe, have you rewired the blocks or changed the numbers? Post a picture of the modbus parameters DB as well. Regards. |
This contribution was helpful to
1 thankful Users |