Joined: 10/7/2005 Last visit: 9/23/2024 Posts: 3022 Rating: (1054) |
Hello Ahmed I'm afraid to say you can NOT use your IM308B (6ES5 308-3UBxx) with the S120 (unless you'll find a COMET200 useable typefile for it) and will need to use an IM308C (6ES5 308-3UCxx)together withCOM Profibus V5.x for the configuration. Below area few links with more on this and I hope it helps: Configurable DP-slaves for IM 308B What are the differences between the DP master interface IM 308-B and the successor product IM 308-C? ET 200 Distributed I/O System with IM 308-C manual |
Cheers |
|
10/3/2011 2:56 PM | |
Posts: 344 Rating: (50)
|
Both MASTERDRIVES & SINAMICS S120 use standard PROFIBUS communication protocols. So the same PROFIBUS interface module can be used in both casees. The new PROFIBUS interface will need to be reconfigured to talk to S120 drives: different hardware = different GSD files, different data = telegrams. The logic will, most likely, will need to change some too. Control word structures are very similar between MASTERDRIVES & SINAMICS, but, depending on the application, there may be programming changes from one drive system to another. Also see forum post on telegram differences |