Hello, be aware that the cyclic profinet frames (I/O data) are tagged Ethernet frames with a VLAN tag. The VLAN Tag has VLAN-ID = 0, and a priority of 6. The switch may not drop these frames, but forward these according with the requested priority. The settings needed are very similar to the settings required for VoIP phones using 802.1p. If you want use VLANs, pay attention to the followinf FAQ http://support.automation.siemens.com/WW/view/en/24947500 Another topic is that some discovery frames sent by the controller are multicast frames. The switch may not drop these frames either. |
Last edited by: edr at: 2/24/2009 7:59 PMBest regards |
|
2/25/2009 11:25 AM | |
Posts: 2 Rating: (0) |
Thank you very much !! |