Dear
find my answer
OK. I assume it was all working before and we are fault finding. First thing to do is check the CPU diagnostic buffer. Also check the diagnostic of the CP itself. Can you please upload them? CPU and cp diagnostic buffer attached .
Is the connection which "Not Set Up" going to the partner directly or via a network device? its not going directly to the partner , it goes with patch panle where our all PLC network connected through server Is there something connected to the same subnet with the IP address? Yes one more PLC conected but that communication fine ( attached photo ) Is the remote partner connected up? yes remote partner is healthy. Are both of the CP card are in RUN mode? All are fine . Attachmentall details.docx (96 Downloads) |