10/5/2017 2:15 PM | |
Joined: 11/25/2016 Last visit: 11/9/2023 Posts: 8 Rating:
|
Hi! I´ve configured a S120 Control Unit with 2 drives+ 2 encoders and carried out commisioning of the motors correctly. I´ve configured telegrams in TIA portal and Starter as you can see in the attached picture. I can read from plc the signals of the first telegram but I can´t write on it. I can´t read or write the other two telegrams. Thanks in advance Attachmenttelegrams.zip (204 Downloads) |
10/6/2017 11:36 AM | |
Joined: 10/11/2006 Last visit: 12/6/2023 Posts: 5718 Rating:
|
Hello, when you want S7-1500 wit S120 (Starter) you have to create the GSD out of the starter project. https://support.industry.siemens.com/cs/ww/en/view/92022677 |
With best regards, |
|
10/6/2017 12:14 PM | |
Joined: 5/12/2006 Last visit: 12/6/2023 Posts: 21954 Rating:
|
the link is not for GSD! This link pointed to the GSDML Generator which generate a PROFINET GSDML File! But here the CU320-2 DP is connected with PROFIBUS to the S7-1500 , so the Generator can't create any helpfull file! |
12/5/2017 3:44 PM |
|
Posts: 6 Rating:
|
This is ridiculous |
12/5/2017 4:04 PM | |
Joined: 5/12/2006 Last visit: 12/6/2023 Posts: 21954 Rating:
|
what exactly ? |
5/22/2020 7:56 AM | |
Joined: 6/19/2017 Last visit: 12/6/2023 Posts: 7588 Rating:
|
New question published by TTundra is split to a separate thread with the subject how STARTER and TIA PORTAL work with one another. Best regards |