hello, For me it looks like you have some problem on the profibus itself like electric potential or double addressing. Did you check the grounding of your system like PE terminal of SIMOCODEpro and grounding of the PROFIBUS shielding? Did you check the parameterization of your SIMOCODE devices to see if all devices have the correct parameterization with own PB address? At the situation where you managed the communication with 4 SIMOCODEs was it possible to replace one of these with the not-communicating one (with changing of the PB address)? |