Hello Atul; I do not know of a ET 200S Ethernet CP that you could use in this case. That I know of, you would have 2 choices: - use an IE/PB PN coupler to interface between the Profibus port of the IM 151-7 and the Profinet interface on your SCADA PC: https://support.industry.siemens.com/cs/us/en/view/19299692 - replace the IM 151-7 by a IM 151-8, which has an integrated Profinet port. https://support.industry.siemens.com/cs/ww/en/view/47409312 Hope this helps, Daniel Chartier |