you can not combine TCON and AG_SEND. Please have a look at the following manual: https://support.industry.siemens.com/cs/de/en/view/78028908 I suggest you to use the PUT/GET function blocks. you only have to insert an unspecified connection to your master PLC and then you can get data via PUT/GET from your PLCs. note: from how many PLCs do you want to get data? please have a look at the quantity structure for the connections of your master PLC. |