Posts: 487 Rating: (45) |
Sinec L2 does not exist any more in the market. It has transformed into Profibus. What master are you using? The first thing you need is the GSD file for the CPU so that you can insert the CPU as a slave in Com profibus. You can get the gsd file from the link below. http://support.automation.siemens.com/WW/view/en/113652 Then you can do the configuration on the master side using Com profibus. But you also need to configure 315-2DP (slave side) usign Step7. A sample configuration is givenin the link below. This uses IM308C as master and 315-2DP as slave. Your configuration should be very similar. http://support.automation.siemens.com/WW/view/en/6709721 |
10/1/2008 11:29 PM | |
Posts: 5 Rating: (0) |
The master is a S5 CPU948, the S7 configuration is ok and in the COMPROFIBUS too but i have to configure something in the DB1 of the S5 am i correct? |
10/2/2008 9:57 AM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Hi Read this Using IM 308C in AG S5-115U/H/F and specially ID: 1142470.(part 6.1) best regards |