3/25/2009 4:48 AM | |
Posts: 12 Rating:
|
?? |
3/25/2009 4:51 AM | |
Posts: 12 Rating:
|
? |
3/25/2009 8:52 AM | |
Joined: 3/21/2006 Last visit: 4/12/2023 Posts: 10221 Rating:
|
Hello 1. Message 288:80 - Both name for PC Station in Simatic Manager and in Station Configurator editor must be the same. Check the station name in the Station Configuration Editor. The name of the PC station in the project must be identical with the station name in the Station Configuration Editor. 2. message 4502:298 - It is possible that the load of the SDBs was not complete or incorrect, with remedy - Make a reset of the CPU modul and load the hardware configuration of the offline project again. 3. message 4502-625 - There has something wrong in your hardware configuration. I suggest you to delete every configuraion, delete this project, restart the PC and start again. You can use instructions from How do you configure a PC station as PROFINET IO controller for connecting to a S7 station (as PROFINET IO device) for the SIMATIC NET OPC server with the SIMATIC NET PC software? Hope this will helps. best regards |
3/25/2009 2:26 PM | |
Posts: 12 Rating:
|
thank you |