5/26/2014 10:14 AM | ||||
Joined: 11/21/2007 Last visit: 3/14/2024 Posts: 2323 Rating: (306) |
Hello AsAPLC Width of Active Bus Module for Power Supply = 97mm Width of 6 Nos. Active Bus Modules for SMs = 6x80 = 480mm Total Width = 577mm These will not fit on 530mm DIN Rain ( 6es7195-1gf30-0xa0 ) You need 620mm DIN Rail : 6ES7195-1GG30-0XA0 - ET200M, RAIL 620MM May be a Bug in the System Configurator Hope this helps Cheers Navnag |
|||
There is no such thing as the last bug in a program |
||||
This contribution was helpful to2 thankful Users |
5/26/2014 11:25 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
Very good " calculated " point Navnag! About bug in Configurator perhaps you could make a new thread and everybody who is using that configurator to share...
|
Last edited by: UMENCHO at: 5/26/2014 2:02 PM |
|
5/26/2014 1:32 PM | |
Joined: 11/21/2007 Last visit: 3/14/2024 Posts: 2323 Rating: (306) |
Thanks UMENCHO BTW - Have you asked Moderator to Hide the "Thanks" button from your posts Dear AsAPLC As suggested by UMENCHO, you should start another thread with the exact details of your problem ( With exact version of Configurator ) so that the Bug if anycan be removed in the next update. Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
5/26/2014 2:16 PM | |
Joined: 10/19/2012 Last visit: 4/17/2022 Posts: 315 Rating: (9) |
Which configuration tool are u using? TIA Selection tool? |
5/26/2014 2:32 PM | |
Posts: 9 Rating: (0) |
TIA selection tool 3.0.0.7 but i also checked with the online TIA selction tool with the same result V6.0.1.0
|
5/26/2014 3:42 PM | |
Joined: 10/19/2012 Last visit: 4/17/2022 Posts: 315 Rating: (9) |
Then it must be a bug in TIA Selection tool. . |
This contribution was helpful to1 thankful Users |
5/27/2014 5:00 PM | |
Posts: 165 Rating: (19) |
There are so many bugs in TIA softwares..... but system seems to be stabilize naw a days....
|
This contribution was helpful to1 thankful Users |
5/27/2014 8:35 PM | |
Joined: 10/19/2012 Last visit: 4/17/2022 Posts: 315 Rating: (9) |
We can do nothing except hope that programmers at SIEMENS do their jobs error free instead of releasing Service Packs & Updates after a while |
This contribution was helpful to1 thankful Users |
5/27/2014 9:03 PM | |
Joined: 11/21/2007 Last visit: 3/14/2024 Posts: 2323 Rating: (306) |
Hello ... Pl see UMENCHO's Post
I can say from my personal experience that they Do Listen and take corrective action which we see in the form of Hotfixes and Service packs Cheers Navnag |
Last edited by: Navnag at: 5/27/2014 9:03 PMThere is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
5/27/2014 9:06 PM | |
Posts: 9 Rating: (0) |
I've sent the problem to the online support i hope they could make an update |
This contribution was helpful to2 thankful Users |
5/27/2014 9:48 PM |
|
Joined: 10/19/2012 Last visit: 4/17/2022 Posts: 315 Rating: (9) |
I agree that they take corrective action my point is that they should not make mistake in first place
|
5/28/2014 5:15 AM | ||||
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (835) |
Hello AsAPLC Width of Active Bus Module for Power Supply = 97mm Width of 6 Nos. Active Bus Modules for SMs = 6x80 = 480mm Total Width = 577mm These will not fit on 530mm DIN Rain ( 6es7195-1gf30-0xa0 ) You need 620mm DIN Rail : 6ES7195-1GG30-0XA0 - ET200M, RAIL 620MM May be a Bug in the System Configurator Hope this helps Cheers Navnag Hello, As Navnag told Width of any bus unit is 97 mm. But when you install bus units on the racks, part of it is being inserted into the next bus unit. Please look at attached picture. Siemens provides Racks suitable for insert / remove function in many widthes.
Hope this helps. |
|||
Ayman Elotaify |
||||
This contribution was helpful to1 thankful Users |
5/28/2014 7:49 AM | ||||
Joined: 1/17/2010 Last visit: 4/18/2024 Posts: 77 Rating: (5) |
dear ayman, you have mentioned that both racks 483 and 530 are suitable for 5 bus modules, but what i know that 483 rack is ok for 4 bus modules and 530 rack can fit 5 bus modules. please clarify. good luck
|
|||
5/28/2014 8:12 AM | |
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (835) |
Hellomostref You need 417 mm to install 5 bus modules. So if you installed them on the 483mm rack, the free space would be (483-417) = 66 mm. Please revise my explanation bellow which I published in previous post.
|
Last edited by: Ayman Elotaify at: 5/28/2014 8:17 AMLast edited by: Ayman Elotaify at: 5/28/2014 8:14 AMLast edited by: Ayman Elotaify at: 5/28/2014 8:14 AMLast edited by: Ayman Elotaify at: 5/28/2014 8:13 AMAyman Elotaify |
|
5/28/2014 8:14 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
If you take a look at calculations everything is clear! I don't think someone would explain you better than the numbers.
|
Last edited by: UMENCHO at: 5/28/2014 8:15 AM |
|
This contribution was helpful to2 thankful Users |