12/29/2020 4:49 PM | |
Posts: 18 Rating: (5) |
Im new to wiring up PLCs. Have been looking around and finding some wire diagrams, but i wanna double check here first so i dont mess up the new LOGO i bought. I have bought this sensor https://www.finglai.com/products/sensors/capacitive-proximity-sensors/LJC18A3-B/LJC18A3-B-Z_BX.html What unclear is how to connect the wires to the logo when using a NPN sensor with 3 wires. One plan was to connect the black to my input, and then blue to the M (minus) of the PLC, and then brown to the 24+ (L+) and also to the GND (FE) of the PLC. Is that somewhat correct? Im also using siemens 230/24V powersupply to get 24v to the PLC, so its connected with 3 wire 230VAC into the power supply. I took the GND (PE) of the 230VAC power cord and connected it into the FE GND of the PLC, hope thats ok. I could have gone and used regular non grounded 230VAC cable, but i felt more safe using extra gnd wire from 230 socket into the PLC I need to get some directions prior to turning on the power how this sensor should be wired up =) |
Last edited by: Japmaco at: 12/29/2020 16:50:00 |
|
12/29/2020 4:53 PM | |
Joined: 12/18/2014 Last visit: 1/16/2025 Posts: 34501 Rating: (4306)
|
The link doesn't work. |
12/29/2020 5:38 PM | |
Joined: 12/18/2014 Last visit: 1/16/2025 Posts: 34501 Rating: (4306)
|
See attachment.
Attachment24 VDC sensor with open collector NPN to LOGO! I5.pdf (446 Downloads) |
12/29/2020 5:50 PM | |
Posts: 18 Rating: (5) |
Thanks. No wonder the confusion.. This drawing is saying.. connect e 2.2k resistor from the black wire to my input to 24VDC... |