5/22/2023 5:35 PM | |
Joined: 12/18/2014 Last visit: 6/16/2024 Posts: 33199 Rating: (4105)
|
Use the F/I converter. |
5/22/2023 6:27 PM | |
Joined: 12/18/2014 Last visit: 6/16/2024 Posts: 33199 Rating: (4105)
|
And with your small informations is a help not possible. |
5/22/2023 6:31 PM | |
Joined: 12/18/2014 Last visit: 6/16/2024 Posts: 33199 Rating: (4105)
|
Show us your program. We want see what you have make to read the value. |
5/22/2023 6:40 PM | |
Joined: 12/18/2014 Last visit: 6/16/2024 Posts: 33199 Rating: (4105)
|
You know that the LOGO! 8.1 or newer can only connect to Modbus TCP/IP, not to Modbus RTU or Modbus ASCII? |
5/22/2023 6:46 PM | |
Joined: 5/22/2023 Last visit: 5/29/2023 Posts: 8 Rating: (0) |
received a strange value |
5/22/2023 6:52 PM | |
Joined: 12/18/2014 Last visit: 6/16/2024 Posts: 33199 Rating: (4105)
|
The LOGO! has by the Modbus addresses an offset of +1. Try to read the the HR19 (with to words) instead of HR18. |
5/22/2023 6:58 PM | |
Joined: 5/22/2023 Last visit: 5/29/2023 Posts: 8 Rating: (0) |
Works! reads integer value, how to read decimal value? |
5/22/2023 7:20 PM | |
Joined: 5/22/2023 Last visit: 5/29/2023 Posts: 8 Rating: (0) |
how to read the remaining value? |
5/22/2023 8:08 PM | |
Joined: 5/22/2023 Last visit: 5/29/2023 Posts: 8 Rating: (0) |
it should be around 500-600 right now |
5/23/2023 2:18 AM | |
Joined: 12/18/2014 Last visit: 6/16/2024 Posts: 33199 Rating: (4105)
|
You select the wrong address and type in the data table. You must enter VD0 as address and Float as type. |