Hello Guys, I have PLC s7-1500 and MTP 700. I have a issue that I don't connect PC, PLC, HMI via PN/IE. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/06/2023 05:24:32New subject after splitting |
|
3/8/2023 7:48 AM | |
Joined: 7/19/2022 Last visit: 4/23/2025 Posts: 436 Rating:
|
Hello Vanhung123, Check the following settings. In the panel: -Check that the transfer mode of the panel it's automatic (in case it is in manual mode you must put the panel in transfer mode when charging). -Check the transfer protocol (PN/IE) and the IP of the panel it's in the same subnet of the PC. In the en engineering PC: -Cehck that the IP of your PC it's in the same subnet of the panel. Try to perform a ping. -Check the PG/PC settings. Select your network adapter with the protocol TCPIP.1. -In the advanced load menu select the same protocolo that you selected in the panel (PN/IE). |
If this Information really helps, you could use the Rate function |
|