3/3/2016 3:55 PM | |
Posts: 52 Rating: (1) |
hello , kindly how can i connect s7-1200 to rotary encoder with (A,B,Z) output phase ? i want use it to count number of motor rotation . thanks |
3/7/2016 9:59 AM | |
Posts: 52 Rating: (1) |
my encoder type is " Autonics E50S8-150-3-T-24 "
please can help me to set the parameters in attach to get the revolution number thanks |
3/8/2016 1:47 PM | |
Posts: 52 Rating: (1) |
i have CPU S7-1200 1214C DC/DC/RLY and encoder "E50S8-150-3-T-24" i want to find the number of encoder pulse ? any help please ? |
3/8/2016 4:02 PM | |
Posts: 5225 Rating: (1185)
|
First a correction.. now that I understand what you want to do - you do not need to connect the Z-phase. Connect only the A and B phases to the appropriate inputs as configured in the hardware configuration. Below a screen capture of the hardware configuration focussed on a sub theme on the HSC.. My recommendation is to go through all the portions of the hardware configuration that relates to the HSC. By hovering on a topic in the hardware configuration, a tool tip appear that allows you to click to jump to in-software help. Extensive help is available: Now the reason for my 1st image.. To read the actual count you have to read ID1000 (if configured as image 1).. that is input double integer address 1000. Ensure you have a tag named for it, example "myHSC" defined as DINT datatype linked to address ID1000. A recent discussion might be helpful: Regards. |
This contribution was helpful to1 thankful Users |
3/10/2016 8:41 AM | |
Posts: 52 Rating: (1) |
Done . everything works well i'm really happy right now thank u very much Mr. William , i'm grateful to your help . |
10/10/2020 5:00 PM | |
Posts: 1 Rating: (0) |
i think you should config the time of filter input to micros to advoid lossing pulse |