Dear sir, i want to connect s7 300 as a master & 128 s7 1200 plc as a slave ,is it possible or not plz suggest me. Thanks
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 5/27/2015 12:34:40 PMNew subject after splitting |
|
5/27/2015 12:53 PM | |
Joined: 5/12/2006 Last visit: 3/21/2025 Posts: 22596 Rating:
|
Hi,
Master -> Slave = Profibus >> not possible (max. 126 Slaves) |
5/28/2015 9:31 AM | |
Posts: 98 Rating:
|
Hello, as i see the conversation was Split from s7-1200 connect to s7-300 via profinet. So i suggest you want to run a controler-device communication on profinet. In that case it´s possible. Note : S7-1200 requires firmware 4.0 to be configured as I-device. Which IO controllers and IO devices support the following functions in STEP 7 (TIA Portal): IRT, prioritized startup, MRP, MRPD, PROFIenergy, Shared device, MSI/MSO, I device, Isochronous mode, System redundancy and Option handling? -> https://support.industry.siemens.com/cs/ww/en/view/102325771 kind regards |