8/10/2015 12:32 PM | |
Posts: 28 Rating: (3) |
Hi experts. I would like to ask some question. Can I connect three wire pressure sensor atlas copco 1089 0575 51 (ecactly is a pressure transducer) to Logo 0-10V Analog input, This transucer operate at 0,5-4,5V range. It have wires: Signal, GND and V+ I try to connect this in different ways, but the value never increase with the pressure that I see on the analog manometer
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 8/10/2015 12:52:12 PMNew subject after splitting |
|
8/10/2015 4:11 PM | |
Joined: 12/18/2014 Last visit: 9/19/2024 Posts: 33799 Rating: (4199) |
What is the range of the sensor? For which logo? |
8/10/2015 10:28 PM | |
Posts: 28 Rating: (3) |
The sensor range is 0-10 bar and logo is 6ed1052-1md00-0ba6 |
8/10/2015 10:51 PM | |
Joined: 12/27/2006 Last visit: 8/18/2024 Posts: 1197 Rating: (113) |
Yuo have to make some calculations. The sensor = 0,5 V to 4,5 Volt, and your LOGO works 0 - 10 Volt. Range 0,5V to 4,5 Volt = 4 Volt 0-10 Bar. If the sensor works with a range of 10 Volt, the sensor must be 10/4x10= 25Bar The sensor starts at 0,5 Volt (not at 0 Volt) 0,5 Volt in a range of 25 Bar = 1,25 Bar. So the offset must be - 1,25 bar The end range of the sensor is 25 Bar (Range) - 1,25 Bar (Offset) = 23,75 Bar So are the settings of the analog amplifier block.
AttachmentCircuit Diagram2.zip (477 Downloads) |
8/10/2015 11:11 PM | |
Posts: 28 Rating: (3) |
Thank You very much |
8/11/2015 6:48 AM | |
Joined: 12/18/2014 Last visit: 9/19/2024 Posts: 33799 Rating: (4199) |
Here's another solution proposed by me. Attachmentpressure_0-10_bar.zip (472 Downloads) |
8/16/2015 11:55 AM | |
Posts: 28 Rating: (3) |
Thank You experts. This is my solution for this machine and probably for the most of air compressor. The Q1 and Q2 outputs are responsible for star-delta motor start. The Q4 output is responsible for load/unload valve The Q3 output is the stop function. AI2 is for PT1000 temperature sensor Will be greate, if someone want or can improve this. Attachmentair_compressor.zip (311 Downloads) |
Last edited by: germynator at: 8/16/2015 3:58:01 PMLast edited by: germynator at: 8/17/2015 12:47:31 AMLast edited by: germynator at: 8/17/2015 12:47:53 AMLast edited by: germynator at: 8/17/2015 8:22:00 PM |
|