Dear all, Any Update. Best Regards, |
4/19/2018 1:22 AM | |
Joined: 9/27/2006 Last visit: 4/19/2025 Posts: 12346 Rating:
|
Hello Mahmoud; Since there are no drivers for SNP in WinCC v14, you will need to use an OPC server. In the doculent below you can e¸determine the type of OPC server, based on the pltform you are using, Runtime SCADA or panels. https://support.industry.siemens.com/cs/ww/en/view/109747181 You can then look for an adequate OPC Server form Matrikon, Top Server, Kepware... Hope this helps, |
Last edited by: dchartier at: 4/19/2018 1:23:22 AM |
|
This contribution was helpful to
2 thankful Users |
4/19/2018 12:18 PM | |
Joined: 3/16/2014 Last visit: 10/14/2021 Posts: 120 Rating:
|
In TIA 15.0 you can also connect to Fanuc I think using the OptionPack: SINUMERIK - Create MyHMI. I do not know if this kind of connection is what you are looking forward. https://support.industry.siemens.com/cs/ww/en/view/109752377/105703147019 |