Hello: |
Last edited by: O_Moderator at: 4/26/2010 1:34 PMnew subject after splitting Last edited by: shr4plc at: 4/24/2010 8:46 AMLast edited by: shr4plc at: 4/24/2010 8:38 AM |
|
4/24/2010 10:56 AM | |
Joined: 10/7/2005 Last visit: 1/24/2025 Posts: 3032 Rating: (1059)
|
Hello shr4plc
I'm afraid this is not possible (well, it would be physically possible but unlikely to work). 32 is the maximum number of Devices per RS485 Segment, so you will need repeaters(or OLM's if you want to go down the fiber optic path) Anyway, the manual below contains a wealth of information about Profibus Networks andis a good starting/reference point for the design process: SIMATIC NET PROFIBUS Network Manual System Manual [schnippschnapp] I hope this helps |
Last edited by: O_Moderator at: 4/26/2010 1:36 PMCheers |
|