11/24/2008 8:47 AM | |
Joined: 9/27/2006 Last visit: 4/25/2024 Posts: 12257 Rating: (2665) |
Hello Dinesh; You will be able to locate all your required information on the Siwarex MS on the following manual: http://support.automation.siemens.com/WW/view/en/22600601 In particular, for your specfic question: SIWAREX MS is an analog expansion module running in the SIMATIC S7-200 automation system. The maximum possible number of SIWAREX MS expansion modules per rack corresponds with the maximum number of expansion modules of the respective CPU type according to the S7-200 system manual. CPU type Max number of SIWAREX MS CPU 222 2 CPU 224 4 CPU 226 7 Table 4-1 Expansion module in the S7-200 system The utilization of other expansion modules can reduce the permitted number of SIWAREX MS. Check the current requirements on the expansion bus according to the S7-200 system manual. Note, Chapter 11.3 discusses current consumption for the Siwarex MS: Current consumption 5 V from the SIMATIC Bus Typical < 140 mA Table 11-3 Data: Power supply from the SIMATIC Bus Hope this helps, Daniel Chartier |
11/25/2008 10:06 AM | |
Posts: 15 Rating: (0) |
Thanks Daniel |