5/16/2016 4:19 AM | |
Joined: 9/27/2006 Last visit: 3/26/2025 Posts: 12344 Rating:
|
Hello Vipz; You need some kind of Profibus master to read the satus and diagnose the Profibus network. A CP 5712 will give you access to the Profibus network, but will not generate the software functions required to turn the PC into an actual Profibus master The easiest way of course would be to have access to a S7 CPU with Profibus master interface, that you could configure with Step 7 or TIA Portal for this test. The only other option would be some version of a Profibus master simulation program. Pepperl & Fuchs, Anybus and others provide this, but it must generally be purchased, along with their own access card for Profibus. Siemens to my knowledge does not sell one. Here are some links from the web: PROFIBUS master simulator VAZ-PB-SIM - Pepperl+Fuchs PROFIBUS Master Simulator - Bihl+Wiedemann GmbH Profibus-DP/DPV1 - Master Simulator - Anybus Hope this helps, Daniel Chartier |