1/3/2018 10:03 AM | |
Joined: 4/28/2015 Last visit: 2/7/2024 Posts: 10533 Rating: (818) |
Hello, I recommend S7-200 System manual (link): S7-200 System manual Start check from page 439 about connect sensor due your module and from page 445 about RTD module description/cfg. In generally in main menu of MicorWin PLC->Information you can see global info about CPU, modules and also addresses depended to each modules. IW addresses are your choice in this case, with this address you can see value of your sensor and make required operation like MOVE and also other maths. |
With best regards... |
1/4/2018 6:18 AM | |
Posts: 10 Rating: (0) |
Hello. both the programming and configuration of the dip switch of the module EM231 performs it on the basis of two pdf I found here in the Forum I upload these pdf with the image of the dip switch, as well as the reading of the rtd in microwin, said temperature value does not match with the ambient temperature Attachmentrtd-module.pdf (472 Downloads) |
1/4/2018 6:20 AM | |
I had to upload the pdf and image by parties
Attachmentpt100_real.pdf (311 Downloads) |
1/4/2018 6:21 AM | |
I had to upload the pdf and image by parties |
1/4/2018 6:23 AM | |
1/5/2018 6:57 PM | |
Thank you already achieved to give solution |