hi, when you want to establish a HMI-connection over Profibus, the CPU-interface needs to be a Master. C1242-5 is a Profibus Slave Module. So a HMI-connection is not possible. you need the Profibus-Master module: COMMUNICATION MODULE CM 1243-5 hope this helps, regards, |
FCK WAR! |
|
This contribution was helpful to
1 thankful Users |
4/27/2018 8:18 AM | |
Joined: 4/28/2015 Last visit: 3/26/2025 Posts: 10837 Rating:
|
Hello, as is on CP 1243-5 Master module manual, only this module can make connection with OP (page 10): CP 1243-5 Profibus Master Module Manual For CP 1242-5 Slave Module check pls page 9 for connection possibilities: CP 1242-5 Profibus Slave Manual |