Hi! I have 8 PLC s7-1200 I want to make that 1 PLC s7-1200 polled sequentially 7 PLC s7-1200 How to do this help?
|
3/14/2018 2:44 PM | |
Joined: 9/8/2011 Last visit: 3/13/2025 Posts: 537 Rating:
|
I've used Get and Put to do that job. You have to check a box in the 1200 HW config to allow com via Get and Put (since StuxNet). And set up exchange between DB's. Here is a link to get started: https://support.industry.siemens.com/cs/us/en/view/1819293 |
Last edited by: Jen_Moderator at: 3/15/2018 9:35:39 AMOptimized link. A smart person learns from their mistakes |
|
3/15/2018 9:36 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating:
|
New question published by AutoGen_940063 is split to a separate thread with the subject Connection between multiple PLCs. Best regards |
3/15/2018 8:02 PM | |
Joined: 11/16/2012 Last visit: 11/29/2024 Posts: 307 Rating:
|
Have a look at this Siemens Application Example: Data synchronization over open communication between multiple field devices (S7-1200) and a head PLC (S7-1200/ S7-300/ WinAC) (Set 17). I think this is what you are looking for. |