10/31/2024 7:49 AM | |
Joined: 4/24/2006 Last visit: 4/30/2025 Posts: 8974 Rating:
|
Hello, Have you seen this faq: No connection to PLC after WinCC Panel Images V17 Update 6 Check or change Date and Time on HMI panel. Do you have an Alarm View which show the Alarm buffer? Perhaps you can find information why connection is not working. Best regards, Wizard |
This contribution was helpful to
1 thankful Users |
11/30/2024 4:52 PM | |
Joined: 2/3/2022 Last visit: 4/11/2025 Posts: 2 Rating:
|
Hi all, The problem was in the HMI date and time It´s working well now.Thanks. Eliseu Ferreira |