Hello, In the online help of step7, you will already find explanations about resources. With some small pictures how many resources are used when you run over a CP. The resources you speak about are resources for S7 connections A CPU has a certain amount of S7 resources (documented in the technical data). If you take a CU315-2 DP for instance: 16 S7 connections. By default, one is reserved for the PG (but you may configure more) By default, one is reserved foran OP (but you may configure more) The rest can be used in two ways: - for configured connections (via NETPRO) - for S7 Basic communication. Here, you don't configure the connection. The connection is setup dynamically at demand and the resource is only used at that time. You can reserve a certain amount of resources for these dynamic connections (to avoid that you configure too much connections in NETPRO, which could leasto a lack of resources for dynamic connections). Special blocs are used (X-PUT, X-GET, ...) and also limited data volumes only are possible. And S7 Basic connections can only be run over MPI. The total of all configured/used resources can not be more than the 16 available in my example. Have a look to this system manual "communication with SIMATIC": http://support.automation.siemens.com/WW/view/en/25074283 |