Hello, Error "8" means "access error at partner plc". So my first question is: Do you allow the access via PUT/GET in the Properties of plc? Otherwise, a PUT/GET access is not possible. (see attachment) A FAQ to yout topic you find here https://support.industry.siemens.com/cs/de/de/view/82212115 |