Industry Online Support
Technical Forum
1/13/2015 9:12 AM | |
Joined: 5/12/2006 Last visit: 2/7/2023 Posts: 21227 Rating:
Hello, take a look in capter 3.3 of the commissioning manual S120. Each motor module is a Drive Object in the CU320-2. For each Drive Object you can configure a seperat telegram slot in the communication overwiew of the SINAMICS S120 in starter. after the configuration transfer the telegramms to hwconfig with starter and then you have a I/O Slot for each MotorModule in you PLC adress space. Regards Christoph |
This contribution was helpful to
1 thankful Users |
Follow us on