Hello, you need CDS (Command data Sets). 13.5 Data sets https://support.industry.siemens.com/cs/ww/en/view/109763287 13.5.1 CDS: Command data set Binector inputs p0810 to p0811 are used to select a command data set. They represent the number of the command data set (0 to 3) in binary format (where p0811 is the most significant bit). ●p0810 BI: Command data set selection CDS bit 0 ●p0811 BI: Command data set selection CDS bit 1 |
With best regards, |
|
4/18/2019 12:20 PM | |
Joined: 10/11/2006 Last visit: 9/30/2024 Posts: 5909 Rating: (805)
|
Hello, there is only a general info: Working with different data sets (DDS/CDS) https://support.industry.siemens.com/cs/ww/en/view/7379354 |
With best regards, |
|
5/14/2019 11:39 AM | |
Joined: 10/23/2014 Last visit: 3/25/2024 Posts: 201 Rating: (0) |
thank you for your response. my project consists of (smart line module - motor module) both of them controlled by plc by your response i am knowing how to create (CDS) to drive(motor module) . i want to create one for smart line module . when plc fail i can operate both infeed and drive(motor module) thank you |