5/21/2014 8:37 PM | |
Joined: 1/28/2009 Last visit: 4/1/2024 Posts: 6836 Rating: (1359)
|
There are some points regarding your design description:
I hope these comments help |
This contribution was helpful to2 thankful Users |
5/22/2014 1:10 AM | |
Joined: 9/27/2006 Last visit: 4/23/2024 Posts: 12257 Rating: (2665)
|
Hello culebrasx; To add to Hamid's good advice, you could have a look at an integrated PID Temperature Control instruction available in Step 7, FB 58 "TCONT_CP". It should provide a solution to your heating resistors control. See the attachment for a brief description of the pulse output function of FB 58. Start with this manual: FB 58 "TCONT_CP" FB 58 "TCONT_CP" is used to control temperature processes with continuous or pulsed control signals. You can set parameters to enable or disable subfunctions of the PID controller and adapt it to the process. These settings can be made simply with the parameter assignment tool… Application The functionality is based on the PID control algorithm with additional functions for temperature processes. The controller supplies analog manipulated values and pulse-duration modulated actuating signals. The controller outputs signals to one actuator; in other words, with one controller, you can either heat or cool but not both. Look also at these FAQs for guidance: What should you pay attention to with feedforward control on control block FB58 "TCONT_CP"? How can I optimize PID Temperature Control using STEP 7 V5.3 SP2? And possibly this discussion can help also: Question about FB58 "TCONT_CP" Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 5/22/2014 1:24 AMLast edited by: dchartier at: 5/22/2014 1:11 AM |
|
This contribution was helpful to5 thankful Users |