Hello najd; Setting your "slave" CPU as a Profinet i-device (connectef to the "master" as IO-controler) seems the easiest way. You can exchage up to 1440 bytes between them, which would allow the transmission of set points, signals and data between the two. Look at the following Application Example for guidance: https://support.industry.siemens.com/cs/us/en/view/109478798 For information on IWLAN you should start by consulting the following manual: |
Last edited by: dchartier at: 05/03/2019 01:31:30 |
|
5/3/2019 2:47 PM | |
Posts: 6 Rating:
|
Thank you daniel for your help But can I use the PUTGET after setting the "slave" and the "master" cpu ? |
5/3/2019 2:55 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello naid; PUT/GET instructions are peer-to-peer connections, diferent from Profinet "master/Slave". The important thing if you want to understand PUT/GeETis that they use unilateral connections, that is, they are only configured on one of the partners. If you create PUT and GET functions on S7-1200(1), you create a connection to an Unspecified partner; you do absolutely nothing in S7-1200(2). Also, you can only send and receive 160 bytes between the 2 CPUs over PUT/GET instructions. Follow the hints in the following video (from YouTube): https://www.youtube.com/watch?v=4k_k8GZuUDk Hope this helps, Daniel Chartier |
Last edited by: Jen_Moderator at: 05/06/2019 08:05:08Embedded video. |
|
This contribution was helpful to
1 thankful Users |
5/7/2019 1:43 PM | |
Joined: 8/3/2009 Last visit: 3/21/2025 Posts: 15056 Rating:
|
Hi you also can use an Open User communication like this_ https://support.industry.siemens.com/cs/ww/de/view/109747710 Bye Murof |
If this Information really helps, you could use the Rate function |
|