5/23/2009 1:21 PM | |
Joined: 9/27/2006 Last visit: 6/4/2023 Posts: 12033 Rating:
|
Hello epanella; Under certain conditions (specific rack numbers and use of IM 314) you can une an IM 463-2 in the S7-400 central rack to connect to S5 I/O racks: http://support.automation.siemens.com/WW/view/en/42681 Here is an extract from the S7-400 Module Data Specifications manual describing the Im 463-2(you will find the link in the above FAQ): 7.1 Using SIMATIC S5 Expansion Units in an S7-400Area of Application The IM 463-2 interface module is used for distributed connection of S5 expansion units to an S7-400.You can use the IM 463-2 in the CR of the S7-400. In the S5 expansion unit, you use an IM 314.This allows you to connect the following S5 expansion units to an S7-400: · EU 183U · EU 185U · EU 186U · ER 701-2 · ER 701-3 Accordingly, you can use all digital and analog I/O modules suitable for these Eus or ERs. Maximum Expansion You can use up to four IM 463-2s in one S7-400 CR.At each IM 463-2 interface (C1 and C2), you can connect up to four S5 expansion units in a distributed configuration. You can connect further EUs centrally to the EUs connected in the distributedconfiguration. Addressing of the S5 modules All S5 address areas are available (P, Q, IM3, IM4) Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 5/23/2009 1:23 PM |
|
5/25/2009 8:37 AM | |
Joined: 1/28/2009 Last visit: 11/4/2022 Posts: 6 Rating:
|
thank's dchartier, in case i use this solution to connect I/O to a PCS7 system, is there any possible problem or i have to make attention on something? |