Dear Sir, Good day. We are trying to convert customer Simodrive 611U to Sinamics S120. Current Simodrive hardware are as below : 15U1 : 1)Control Unit : 6SN1118-0NJ01-0AA0 - 1 unit 2) Power section : 6SN1123-1AA00-0BA1 - 1 unit 3) Profibus Module : 6SN1114-0NB01-0AAx - 1 unit 13U1 : 1)Control Unit : 6SN1118-0NK01-0AA0 - 1 unit 2) Power section : 6SN112x-1Ax0x-0BAx - 1 unit 3) Profibus Module : 6SN1114-0NB01-0AAx - 1 unit I have tried to convert to equivalent Sinamics S120 as attached Starter file. 1) May I know whether my conversion correct? 2) Existing Simodrive use Telegram 105. So if I were to change to Sinamics S120, I just need to amend hardware configuration to SInamics using Telegram 105 right? Any modifcation of program in Simotion C need to be done? AttachmentProject1.pdf (83 Downloads) |
2/29/2020 4:40 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, How many axes are controlled? Please provide the information along with the application so as to confirm if selection of CU & CF is correct. Power section MLFB number 6SN112x-1Ax0x-0BAx is incorrect, please provide correct number. 6SN1123-1AA00-0BA1 power section is of 1 axis 25 A. Why you have selected Double motor module 6SL3120-2TE13-0AD0 of 3/3 A capacity? What is MLFB number of installed infeed module. Please provide to confirm selection of line feed module & AC input side elements. Please provide present servo motors MLFB numbers. Do you want to retain those or replace those? HTH |