Industry Online Support
Technical Forum
3/5/2009 3:23 PM | |
Posts: 557 Rating:
|
hi you can update the os of ur hmi. regards vivek |
3/5/2009 4:51 PM | |
Posts: 4 Rating:
|
Thank you for your quick response, I willcheck the OSfrom thepanel. greets, Frank |
3/6/2009 9:54 AM | |
Joined: 4/24/2006 Last visit: 2/7/2025 Posts: 8836 Rating:
|
Dear Wicky, Perhaps you can perform an OS update with option reset to factory settings: See following link: http://support.automation.siemens.com/WW/view/en/19701610 Best regards, Wizard |
3/9/2009 11:00 AM | |
Posts: 4 Rating:
|
Dear Wizard, tomorrowIam goingback to the plant to try the suggestioned options. I will let you now the results. Thanks in advance, Wicky |
3/12/2009 12:55 PM | |
Posts: 4 Rating:
|
The problem is solved There wasa USB stickfrom 4 giga inserted, and the max seems to be 2 gig. Greets, Wicky |
3/12/2009 3:44 PM | |
Joined: 4/24/2006 Last visit: 2/7/2025 Posts: 8836 Rating:
|
Dear Wicky, Thank you for feedback, great you found the solution. Best regards, Wizard |
Follow us on