Hi, I want to monitor a state of motor and store retentive:
About point 1 to 5 there are no problem (see attachment) but I dont understand how store the Hour activation yesterday. Is it possibile? Another question about Hour counter:
Thansk and Best Regards AttachmentTest Counter Forum.zip (67 Downloads) |
Last edited by: roberto.zeni at: 01/04/2021 14:38:03 |
|
1/4/2021 4:49 PM | |
Joined: 12/27/2006 Last visit: 11/27/2023 Posts: 1192 Rating:
|
Yes, the Hourcounter counts only hole minutes. If its a problem use one of this counters. The first counts hole seconds, and if that not enough, the second counter counts 0,1 sec. AttachmentUrenteller.zip (69 Downloads) |
1/4/2021 5:09 PM | |
Joined: 12/18/2014 Last visit: 11/29/2023 Posts: 31498 Rating:
|
In attachemt a possible solution for storing runtime of yesterday. Take a look at the Parameter-VM-Mapping. The counter value is a DInt. Values smaller 32.768 are in the right word of the DWord (in example VD0). The right word is VW2. AttachmentStoring_runtime_yesterday_8.3.zip (81 Downloads) |