Short answer, but not satisfying for you of course: You cannot! TM PosInput requires either SSI signals, or signals according to RS422/TTL, see here:https://support.industry.siemens.com/cs/de/en/view/109780353/132722229643 If you only have a pulse and nothing else, and this is 24V, then TM Count would be te right way to go. Pretty similiar to TM PosInput, but can work with this signal as it does not necessarily need the differential signals like TM PosInput. Regards, |