9/10/2014 6:38 PM | |
Posts: 3093 Rating:
|
It is for sureimpossible to make the CP341 Modbus driver work with this. Regards, Kaulquappe |
This contribution was helpful to
1 thankful Users |
9/11/2014 7:14 AM | |
Joined: 12/1/2009 Last visit: 2/9/2025 Posts: 672 Rating:
|
Dear dzwilu, sometimes a second look into the manual or documentation helps. I don't know about the model of meter you have but I read from the manual of the N14thatthe data is availabale in 16bit registers (from 7000...) as well as in 32bit registers from (7500...). So using 7000 instead of 7500 should fix your problem. Best Regards. |