Although the post is a bit outdated, the black plane connection between the CPU and the CP is the bottle neck. It is just 187,5 kBit/s! So it doesn't matter if you use an external CP343-1 or the MPI interface, the performance is the same. The only way to have better performance with S7-300 CPU is using the internal Ethernet / PROFINET interface on the CPU. If doing so, expect update cycle less 10ms. |