12/28/2008 8:42 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (318)
|
Hi Msamy, I think you are working with a 41xFH-system.. The numbered questions above are to answer as following: 1. In a H-System it is not at all necessary to STOP the CPU's if you use active backplains; 2. When you use MODBUS RTU then it is necessarry to load the driver on the CP341, see the link: How do you load a loadable driver (such as CP PtP Modbus Master) into a CP 341 which is connected to an H-system by means of ET 200M?Please look also to the newest drivers and the newest Functionblocks ! Note: This procedure is only necessary for loading the loadable drivers, not for assigning parameters. The loadable driver only has to be loaded into the CP 341 once. With the hardware dongle plugged in, the CP can then be operated with the MODBUS master/slave protocol. You can find further information about these drivers in the manuals on the "MODBUS Slave" (Entry ID: 1218007) and "MODBUS Master" (Entry ID: 1220184). The loadable drivers "CP PtP MODBUS Slave V3.1.3" and "CP PtP MODBUS Master V3.1.2" are available to download on the Internet under Entry IDs: 8715908 and 8713784 respectively. 3. If it is on an active backplain then is there nothing necessary to start the CP341 if everything is loaded well. TIP: If you have a 300-Serie CPU then it is easier to load the driver for MODBUS RTU on this system. Look also if you have the PTP program where all the necessary items are to load the MODBUS-driver. For programming the S7-41xFH you need the following program if you have only a H-System STEP7 V5.4 SP4, if you have also F-System then you need also CFC, SCL and F-Systems. PLEASE be carefull all the mentioned things are fore S7 and might also work with PCS7 but I don't know that... |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|