10/6/2009 12:06 PM | |
Posts: 37 Rating: (2) |
Hi All,
I have read the FAQs and some manual, but I am really confused now!! I already configure S7 313 (6E7313-6CF03-0AB0) to be a master controller for a Festo valve and Vega level transmitter.. That is working fine. Now this PLC has to be slave for a master CPU (OpenPMC104) which is controlling the valves with corresponding to the Level by Vega transmitter. To transfer IOs to the OpenPMC, need IOs mapping which I am trying to sort it out. In the manuals mentioned that i need to use FC1 and FC2 as send and receive, i have tried that, but doesn’t work at all.. Is the CP 342-5 can be a slave for the OpenPMC? If so, how and if possible to see an example please.. Please note: this CP card doesn’t have a configuration tab for communication purposes?? “as you can see in the attachment” Best Regards AttachmentDesktop.zip (100 Downloads) |
10/6/2009 12:31 PM | |
Joined: 8/25/2005 Last visit: 10/5/2024 Posts: 1162 Rating: (111) |
Hello MANS, the CP342-5 is a certificated DPV0-Slave. So every DP-Master which workes with certificated slaves should be able to communicate with the CP. Within the options of the CP you have to select the operation mode DP-Slave. You have to programm the FC1 and FC2 to define the I/O-Data of your Slave. I found an example how to configure the CP to communicate with an S5. I don't know how to do it with your Master but I hope you could transfer the information to your needs. How do you operate an S7-300 CPU (with CPU 342-5) as slave via the PROFIBUS DP with an S5 (IM 308-C) as master? Within the options you will find a diagnostic tool which is very helpfull for this CP. Please inform us about your success. I'm interested in how it works Best regards Sabine |