4/2/2014 8:19 AM | |
Posts: 1368 Rating:
|
Hello, with TIA V13, i could configure your constellation. What engineering software do you use? Do you have one project or two? Greetings... |
4/2/2014 10:51 AM | |
Posts: 80 Rating:
|
Hi! I am using Step7 V5.5. I try to do the 317 side in my project and config the 315 into my profinet network. The 315 part is in an other project... |
4/2/2014 1:11 PM | |
Posts: 80 Rating:
|
I already know that I cannot use the drag&drop.. But how can I create gsd of CPU31x + CP343-1 LEAN? And after creating it, siply install it into the catalog? |
4/2/2014 1:43 PM | |
Posts: 1368 Rating:
|
Ok... you make a projekt in STEP 7, insert a new S7-300 Station and implement the CPU + CP in the Rack. Then mark the station and create a gsd with Options->Create GSD. This new station will be integrated into the HW catalogue. But note: this function is only available at S/-300 CPUs >FW V3.2. An example you also find here http://support.automation.siemens.com/WW/view/en/31764614 More information about the PROFINET I-device function is available in the system manual "PROFINET, System Description" in the chapter entitled "I Device" in Entry ID 19292127. |
4/4/2014 2:52 PM | |
Posts: 80 Rating:
|
Thanks. This sounds good, but the options-> create GSD is always grey for me, I cannopt choose it. What am I doing wrong? |
4/4/2014 3:24 PM | |
Posts: 1368 Rating:
|
You have to activate the I-Device mode (properties of PN-Interface of the PLC). Then the function is available... |
4/9/2014 1:06 PM | |
Posts: 80 Rating:
|
Hi. no matter what I do, I cannot activate the option to create GSD. Is it possible to send some pictures what to do? Thanks! |
4/10/2014 8:23 AM | |
Posts: 1368 Rating:
|
Hello, as i said, you need FW >=3.2 to use the i-device function. I attached a picture which shows the configuration. |