Joined: 3/20/2013 Last visit: 4/3/2024 Posts: 676 Rating: (44) |
The limit are 12 connections, that means if you insist on getting connect to your number of servers you need to 'multiplex'. Connect to a server --> send/receive data --> disconnect --> connect to next server --> ... here the technical data of the cp343-1 lean: http://support.automation.siemens.com/WW/view/en/23523142/td |
Best Regards, |
|
This contribution was helpful to1 thankful Users |
4/4/2013 1:14 PM | |
Joined: 11/8/2011 Last visit: 12/5/2024 Posts: 387 Rating: (43) |
Hi Fafner thanks for the reply do you have any Example or sample project for the multiplex Connect to server--->send/receive data---->disconnect----->connect to next server---->.... Thanks in advance |
12/10/2014 4:39 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
|