1/24/2012 11:14 AM | |
Joined: 8/25/2005 Last visit: 5/25/2023 Posts: 1161 Rating:
|
Hello Dmitriy87, CP342-5 as a DP-Slave, ok, no Problem But I have to say, that a CP 443-5 Basic dosn't support DP-protocol. Have a look at this manual: S7-CPs Manual / Part B3 Description of the CP 443-5 Basic (Teil A siehe Beitrags-ID 1158693) Maybe you try to establish a communication via profibus FDL? Or us a CP 443-5 Extended Here you will find some examples how to establish communication: Quickstart Best regards Sabine |
1/24/2012 5:19 PM | |
Posts: 1547 Rating:
|
Hello, if you don't need the master-slave configuration it's also possible to use simple S7-communication. How many byte do you want to send? https://www.automation.siemens.com/net-static/Quickstart2009/quickstart012003/html_00/profibus/pb_s7_s7_s7.htm The second one should be interesting for you. |