6/10/2006 10:10 AM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (315) |
Hi Jucegarcia, Access can be made via the FB192. [:)] When you want to do it over the I/O then the next possibility is there: This behavior should not occur if words are configured and access is made using word commands. In the case of long consistent areas, you must always observe the instructions given in the device manual "Distributed I/O System ET200", Appendix B7. This manual is available in Entry IDhttp://support.automation.siemens.com/WW/view/en/1142470 Here, the sequence in which access is to be made is defined. The sequence depends on the type of CPU and the area in which the data is stored. The byte that is marked here with a dark bar must always be read or written last. |
Last edited by: Late at: 6/10/2006 10:12 AMI hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|