7/4/2017 7:16 PM | |
Joined: 8/31/2005 Last visit: 1/23/2023 Posts: 2194 Rating:
|
You can use a G120C as drive and a TM Posinput as feedback. If you want to use PROFIsafe, you will have to add (additionally) a Telegram 30 for the G120C in the HW configuration. This is described in chapter 4.4 . This may be usefull to: https://support.industry.siemens.com/cs/ww/en/view/82841762 |
|
|
7/5/2017 7:15 AM | |
Joined: 8/29/2013 Last visit: 1/30/2023 Posts: 20 Rating:
|
Thank you!! |