2/18/2013 7:29 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (713)
|
hello, See attachment: B + , A+ , M , V , I , M. Analog input 2 Analog input 1 common (-) Voltage output Current output common (-) Regards Marcjan Attachments7200_224xp_schematic.pdf (431 Downloads) |
Last edited by: Marcjan at: 2/18/2013 7:29 AMProblem solved? |
|
2/18/2013 10:21 AM | |
Posts: 461 Rating: (29) |
Hello Marcjan, thanks a lot. My requirement was fullfilled, i have 2 doubts 1) I have wired the AI 1 where AI 2 was free & then common. Now i am getting 1.5 v in the AI2 channel where i havent wired anything.When i am changing the channels like wiring AI2 then this 1.5 v was readed in the AI1. I havent tried wiring both channels. 2 ) While using ITR function why 32000 has to be used for the Input High value.Is it like the s71200's 27648 which is the max digital value for representing 20 ma of AI max value Regards, Nelliyan.G |
2/18/2013 11:05 AM | |
Posts: 461 Rating: (29) |
Hi Marcjan, Thanks a lot.. I am set to go Regards, Nelliyan.G |
This contribution was helpful to1 thankful Users |
5/21/2013 5:37 PM | |
Posts: 9 Rating: (0) |
Hello Marcjan, The issue already solved, now I able to use both of Analog input signal. Thank you for your help.
|
This contribution was helpful to1 thankful Users |