5/7/2018 1:46 PM | |
Joined: 4/28/2015 Last visit: 3/26/2025 Posts: 10837 Rating:
|
Hello Pablo, what type of connection, protocol used here? |
With best regards... |
|
5/7/2018 1:50 PM | |
Joined: 12/26/2012 Last visit: 3/27/2025 Posts: 11 Rating:
|
Thanks... I'm using s7 connection and profinet. |
5/7/2018 2:07 PM | |
Joined: 7/9/2015 Last visit: 3/27/2025 Posts: 4210 Rating:
|
Hi, if you use CP343-1 Lean the combination of CP and PLC can be used only as Server, so I think you must use a CP343-1 or CP343-1 Advanced. Please also check manual: CPU-CPU Communication with SIMATIC ControllersRegards, Towome |
|
|
This contribution was helpful to
1 thankful Users |