Hello fahad; The CU 240B-2 has a RS-485 interface for USS or Modbus RTU interface. Using Modbus RTU would be easier (sample function blocks have been designed by Siemens for a CP 341) but comes out more expensive since you need to purchase the loadable driver. https://support.industry.siemens.com/cs/ww/en/view/1220184 Note that our friend TIBI68 has developped his own blocks for Modbus RTU that you can freely download here: Specifically for your initial enquiry: Have a look at the reply from our friend Late in the following discussion on USS protocol using a CP 340: Hope this helps, |