Hello Brinkmann there sure is a way, it does in your case involve using SFC14/15to read/write consistent data from/to the DP Slave. Have a look at the link below which neatly collates all "consistent data" entriesfor moreon this subject: Which entries deal with consistent data in conjunction with distributed I/O? Alternatively, change the setup of each of the 16 Word longI/O Modules from "Consistent over: Module" to"Consistent over: Unit"andthe "TPQ(A)W" should do the job (without the need for SFC 14/15, note that you data consitency is now only guaranteed for each Word by itself rather than the whole module). I hope this helps. |
Cheers |
|